Lithi2-16 Breaker Trips - Trying to use CANBUS and RS485 Simultaneously
I'm having an issue with my batteries tripping the built-in breakers when I try to use both the CANBUS and RS485 communications at the same time - but ONLY if the PC running Ruixu Tools is plugged into AC power.
This is my scenario:
(2) Lithi2-16 batteries connected via standard Ethernet cable, operating for a couple of months without any issue, everything as expected.
The Master battery is connected to a Sol-Ark 12k, state of charge, current flow, etc., is displayed as expected on the inverter.
If I connect an Ethernet splitter (i.e. Deye/SunSunk/Sol-Ark RJ45 splitter from Solar Assistant), plugging the CANBUS into the Sol-Ark and the RS485 into the Ruixu-supplied USB adapter allows communication with both the inverter and Ruixu Tools on a laptop.
BUT if I plug the laptop into AC power via the standard power brick, both batteries immediately trip the built-in breaker and the logo flashes…



I'm having a similar problem, except kind of the opposite.
I have two lithi2-16's paralleled together with a 6000xp as the documentation indicates.
Everything works fine until I disconnect grid power, then both batteries go into emergency stop.
When I say "disconnected grid power', I mean physically remove the wiring (I have it wired to a NEMA L14-30). Turning the breaker off does not cause a fault.